Write the formula for Fault MVA, Fault current, Base MVA.
Answers were Sorted based on User's Feedback
Answer / ariel
- Draw the per phase diagram of the system
- Express all impedance in per unit values
- Choose a common MVA base and express all Zpu on the
selected common MVA base
Znew= Zpu(MVA base/ MVA)
-Calculate the total per unit impedance of the system
using circuit principle
- Calculate the fault power
MVA fault= MVA base/ Z total per unit
I fault = MVA fault/ 1.73* V
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / mak
The fault current of a power transformer will depend on the following;
Transformer Rating (in KVA/MVA)
per unit impedence of the transformer (%p.u.)
line/phase Voltage (VL/VP)
the following formula can be used to find the fault current on the secondary side of a transformer
Fault Current = Transformer Rating /(per unit impedance x phase voltage)
The Values of Transformer Rating, per unit impedance & phase/line voltage will usually be mentioned on the transformer rating plate / data sheet
As an example a 500kVA, 11kV/400V/3-Phase/50Hz transformer with 5% p.u impendence will have the following fault levels on the secondary side
Fault level = 500/(5%)=10000kVA
Fault current = 500/(5% x 400 x 1.732) = 14.4 kA
Remember to use 3phase voltage!
Is This Answer Correct ? | 3 Yes | 4 No |
To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's
how did the differential relay work to protect the power transformer
why the three phase transformer's star point does not sparks or seperated? while we often see that two phases touches each other it sparks and ocationaly conductor breakes out.
Which theory is used in the analysis of salient pole rotor synchronous machines? Who is credited for this developement? Could the same theory be used for cylindrical rotor synchronous machines?
I am about to write exam in RRB bangalore for the post of section engineer.please provide me with previous exam questions
As we know induction squirrel cage motor torque Directly praprortinal to applied voltage in star connection & delta also. If I connect 55KW Motor to DOL starter in load condition does motor withstand the load & what will be the current withdrawn ? motor will not fail ?
I have 1500KVA transformer ,How much Maximum KW Load is allowed?
15 Answers GKC Projects Limited GKCPL,
Why transformer rating in KVA? describe.
Write the force balance equation of m ideal mass element.
What is power relay?
What is the important precuations need tocarried out while working with Electrolite in Battery PM?
What are the commonly used schemes for the bus zone protection?