Answer / mior
First of all, you need to know your total connected load
(TCL). Then, you apply Diversity Factor at your TCL to get
the Maximum Demand (MD).
Example;
You have 1no. 36W Florescent Lighting and 1no. socket outlet
(250W). Your TCL will be (36W + 250W) = 286W.
In actual, the TCL may only contribute certain percentage
for your MD; that's why you need to apply Diversity Factor
(DF).
Common practice, light fitting will contribute 80% and
socket outlet giving 40% for your total MD.
Hence, your total MD will be = [(36W * 80%)+(250W*40%)
]= 128.8W
Therefore, your total MD to be declared for your Utility
Provider will be 128.8W.
The link below might help your for more info.
http://guide4electricalconsultant.com/calculate%
20tcl&md.html
| Is This Answer Correct ? | 72 Yes | 13 No |
Answer / sachin
First try to know what is mean by max demand . Max demamd
is the simutaneous max requirment of power for any unit.
there is no standard practise to calculate the MD of any
unit . but one can carry out as follows.
1] CALCULATE THE TOTAL CONNECTED LOAD .
2] APPLY DIVERSITY FACTOR - IT IS THE PART OF EXPERIENCE
AND MAY VARY FROM UNIT TO UNIT .
3] TOTAL CONNECTED LOAD X DIVERSITY FACTOR = MAX DEMAND
| Is This Answer Correct ? | 27 Yes | 9 No |
Answer / yogish
There is no specific method to calculate the MD from the
CL. It really depends on the following: -
1. Type of industry: Continuous or Batch process, Heavy or
Medium or Small
2. Mechanical load or Heating load or Furnace load
3. Plant at infant stage or stabilised
4. Standby loads included
5. Largest single load and its starting method
6. Possibility of staggering load without affecting
activities.
7. Whether the major motors are optimally sized or oversized
We can get at some figure, only by experience in a similar
industry.
| Is This Answer Correct ? | 41 Yes | 25 No |
Answer / parag nikumbh
MD in KVA = (connected load in kw x Diversity factor) / P.F.
Diversity factor can be calculated as Running load/Installed load
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / j manikanta
Can you clarify my doubt.
we have a Total connected load 100 KW. We want to take an HT Connection in Andhra pradesh. So how much KVA will be sufficient for my plant. Kindly suggest me about CMD.
We will use 80-90% of Connected load. And what is diversity factor. how we need to calculate this
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / kanand078
first calculate the total load in plant. and find the
voltage and current,after u can use this formula and
calculate the MD=V*I
| Is This Answer Correct ? | 24 Yes | 62 No |
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
Why the symbol of register is "zig zag"
why the rating of transformer in only KVA not in others?
What is “pu” in electrical engineering?
WHAT IS THE SHOPE TESTING
why the transformer ratings in kva or mva?
why does in transformer the v/f ratio constant?
Can i use to 3 phase 4 wire energy meter inplace of 3 phase 3 wire energy meter ?
If Two Generators are working parellel in a network and suddenly the field of one Generator get weakened What will happened if there is no reverse power relay fixed in that Generator panel????
star delta advantage and disadvantage?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
difference between the applicability of nortons and thevenin theorem
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)