What is the fuction of UV & how it works in circut breakers?
is it one type of relay?
Answers were Sorted based on User's Feedback
Answer / g.ravikanth
Its an under voltage relay which will breaks the circuit.
when voltage goes under the rated voltage, it will be
physically made of an under volt coil connected to relay
Is This Answer Correct ? | 12 Yes | 2 No |
UV IS Under voltage realease type relay,
uv is installed in breaker and it is designed so that when
the supply of its coil is interupted it opens the breaker.
when you give supply then only you can close the breaker.
it is installed manily for interlocking.
we can use them in almost all type of onload ckt breaker
like-- MCCB,ACB,VCB,SF6 Etc...
if their is any mistake in this answer pls post it,i am diploma holder and working in panel manufacturing co--
Rajendra sawant, miraj...maharashtra.
Is This Answer Correct ? | 3 Yes | 0 No |
UV= Under voltage Coil and this also one type of relay.
In breakars it will sence and give comond to breakar.
I think if the voltage is less than +/-440V or rated
voltage passing through the breakar it will sence.
Mr.Ravikanth as per my knowledgeall the relays will sence
the foult and give comond to breakar for operation.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / vijay
first Relay it will Sence of uv thane relay give comand in
vcb so inst vcb trip
Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate size of cable from motor current given and how to calculate full load current of a induction motor.
how much mininmum length required to conduct a DC Hipot Test on 33kV AC Cable with 45kV DC? Is it 20meter or Less then 20?
can we run the home fan both clock and anticlockwise direction
what is dc mator?types of dc motor?losses in dc motor?what is the mechanical,electrical and commercial efficiency of a dc motor?
if we keep frequency constant can we cal a synchronous generator as a dc generator
Can u tell me design of switch yard
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
What is the difference between PLC & DCS?
What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.
importance of reactive power management
ALL HT /LT PANEL TEST? DISCRIPTION.
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side