why rotor resistance starter is not suitable for
squrielcage induction motor?why it is suitable for slipring
induction motor?

Answers were Sorted based on User's Feedback



why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable fo..

Answer / gajanan

in rotor resistance starter external resistance made
connect across rotor winding to reduce rotor current which
consequently reduce starting current.

in case of sq. cage motor there are rotor conductors short
circuited permenantly at end rings and ext resistance can't
connect across it.

Is This Answer Correct ?    44 Yes 6 No

why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable fo..

Answer / sennapparajan

slip ring motors normally used where ever high stsrting
torque required. by connencting external resistence through
slip rings we can increase the starting torque. so that the
motor designed with slip rings.

at normal case sqrl cage motor will be used. its rotor
conducter shorted permanently./ and to reduce this motor
starting current sar-delta sarters can be used.

Is This Answer Correct ?    16 Yes 7 No

why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable fo..

Answer / umang

in case of SQ motors, the rotors are shorted and in case of
slip ring motors the exterrnal resistance added with rotor
ckt. to get high starting torque along with limiting
starting current.So when the rotor achieves its full speed
hthe resistaces are shorted by slip rings.which help to get
high stating torque.

Is This Answer Correct ?    7 Yes 3 No

why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable fo..

Answer / felixraj

In SQ IM rotor bars are shorted permanently by the end
rings,there was no possibility to vary the resistance.
In slip ring it was a wond rotor so the end terminals are
brought out and R can be easily varied by the help of slip rings

Is This Answer Correct ?    7 Yes 5 No

why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable fo..

Answer / gopi

in squrielcage induction motor the rotor bars are short
circuited. there is no provision of including resistances
on rotor side.
but in slip induction motor, the rotor bars are connected
to slip rings for providing and an external resistances.
thats why tha rotor resistance starter can be used in
only slip ring induction motor.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How much earthing require for h.t.22 k.v. cable in coming side & out going & 22 lighting arrest or,22 k.v.D.o. & A.B. switch.

1 Answers  


what is photo voltic cell,& what are the materials associated with that?and any spcifications like volts/cm etc?

0 Answers  


What is the selection process of breakers. Can any one please give a formulation on same?

0 Answers   Sterling Wilson,


Is it necessary to place tap changer in secondary winding or we can use on both sides?

3 Answers  


which one is the most common system for secondary ditibution

1 Answers  






What is the tests required for a 132 kV, 400 kV , 765 kV for a Circuit Breaker and Power Transformer before commissioning ?

0 Answers   Eprosys Engineering Consultants,


why only 26v dc is used in aircraft and 115v ac in aircraft.

0 Answers   Jet Airways,


i have a Connected Load of 280KW and Maximum Demand of 224KW to one of SMDB under design with me. which criteria should i consider to design panel and main cables connected Load or Maximum Demand 1)Breaker rating 2)Panel Busbar rating 2)Incommer cable sizing (ignore Voltage drop)

1 Answers  


WHAT IS THE REASON FOR LOW VOLTAGE IN HOUSES?*

1 Answers  


a.c&d.c motor&generator

2 Answers   Vizag Steel,


The current though a branch in a linear network is 2A when the input voltage is 10 volts. If the voltage is reduced to 1 volt, and the polarity is reversed, what is the current flowing through the branch ?

2 Answers  


why the value of impedence is taken as %impedence in fault currrent calculation

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)