What is defference between earthed and unearthed cable(HT)?
Which is better for under ground cabling?
Answer / abhinav yadava
Earthed System
 Earlier the generators and transformers were of
small capacities and hence the fault current was less. The
star point was solidly grounded. This is called earthed
system.
Unearthed System
 Today generators of 500MVA capacities are used
and therefore the fault level has increased. In case of an
earth fault, heavy current flows into the fault and this
lead to damage of generators and transformers. To reduce
the fault current, the star point is connected to earth
through a resistance. If an earth fault occurs on one
phase, the voltage of the faulty phase with respect to
earth appears across the resistance. Therefore, the voltage
of the other two healthy phases with respect to earth rises
by 1.7 times. If the insulation of these phases is not
designed for these increased voltages, they may develop
earth fault. This is called unearthed system.
Is This Answer Correct ? | 16 Yes | 8 No |
what is the differance beetwen installation and errection ?
how can we select the appropriate VCB ?
On what basis primary and secondary of a transformer is chosen?
how do you choose the cable size as per amps rating & the voltage drop for the same.
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
how to find diesel consumption of 600kva DG per hours????
how a.c. genarator control power factor when its conected to grid supply by incrising or decresing excitation voltage.
AC covered area by ton calculation
State angle criterion.
What is the cause for a blown fuse in one phase of primery side(HV) of a three phase transformer( 4169v-460v) in the time of closing its supply breaker. There is no load on the secondery side of the transformer in this moment.
operation of protection relay watchdog contact?