Answer / www.islamqa.com
Bharathi is right, we have to use "condensation pot"
# Actually the gas is "self venting" and the instrument
mounting should be above the pipeline in order to avoid
vapor condensation which cuase fault reading.
# For liquid service the instrument mounting should be
below the pipeline as the liquid is "self draining".
# If we want to mount the instrument below the pipeline in
gas service we should use "condensation pot" and the
operator should drain it regularly to avoid fault reading.
# In steam service we use the condensation pot also and it
should be fully filled with water and its mounting should
be in the same pipeline level and the instrument itself
will be below the pipeline, this link indicte the situation:
http://www.eng-tips.com/viewthread.cfm?qid=166893&page=97
the aim of water filling is to provide a solid motion
transfer in order to have a good accuracy.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
CELL.: 00 2 0121367310
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / ravi
you can use the txe down, which measures level or flow, we
have to make impulse line downwards by taking flange
opening at the top of process line. we have to give steam
line over the entire impulse line, so that gas especially
LPG will not condense at atmospherice temp, and it will
give the correct pressure across the diaphram of DP, so
that correct level can be mearure.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / hemant bhati
You can bring the Transmitter down side only when you
provide a diagram seal type of arrangement even there is
gas line.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / snehal
place the taps side of the line
place the transmitter beside/above the line so that
condensed fluid will drain off
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / kk
transmitter taps should be greater than 45 from both taps
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / krishna
YOU CAN INSTALL TRANSMITTER DOWN SIDE SO THAT YOU SHOULD
MAKE IMPULSE LINES ACCORDING TO REQUIREMENT . TRANSMITTER
RANGE WILL CHANGE ACCORDING TO DISTANCE FROM TANK TO THE TX
LEVEL .OTHERWISE ERROR WILL ERAISE
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / bharathi
You can bring the impulse line as you want. But the only
thing is u should provide condensate pot at drain point. al
so provide steam trace over the impulse line. It will
avoided rate of condensate. If you install without this
condensate pot the transmitter reading starts fluctuate
frequently.
Is This Answer Correct ? | 2 Yes | 3 No |
What is Hysteresis mean in Instrument?
What is the main three inputs of DCS?
please explain smoke detectore & lel detector?what is o/p
how do u calibrate the vacuum transmitter if it shows more reading
how micro-processor and micro controller different from architecture
3 Answers Bhushan Power Steel,
How is PH sensor works ?
hello this is dhinakar subramanian. how to piping and instrumenation drawings and also how to create the data sheets...
what are level of automation & how these are distinguished ?
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
Which boiler is use in power plant
what is cascade loop and how it work and why it used instead of PID single loop? In cascade, Which loop is faster and slower? Please explain with loop drawing and example...