Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How do you select a cable size(cu and Al) for a particular load

Answers were Sorted based on User's Feedback



How do you select a cable size(cu and Al) for a particular load..

Answer / manikandan

current rating cable depends upon manufacture (make cu
percentage) for the cable selection first calculate the
cable length and voltage drop,total impedance ect..

Is This Answer Correct ?    4 Yes 2 No

How do you select a cable size(cu and Al) for a particular load..

Answer / gnd kumaran

First calculate the load current.
Then select the cable according to the current carrying
capacity.[To know the current carrying capacity, refer
cables catalog]


Load Current X Length of the cable X Voltage drop per Amps
per Meter [in milli volts]/ 1000
now we will get voltage drop
If voltage drop is below 3- 5 percentage, you can choose
the above cable, if it is more than 3-5 percentage, go to
next higher size and repeat the calculation.

Is This Answer Correct ?    3 Yes 1 No

How do you select a cable size(cu and Al) for a particular load..

Answer / shailesh

conductore size (cu 3A/Sqmm and Al 1A/Sqmm )but in case of
cable it depends on its type of used.for ex-for cu-1sqmm
can take 11A. when it used in pvc conduits in indoor.

Is This Answer Correct ?    3 Yes 2 No

How do you select a cable size(cu and Al) for a particular load..

Answer / pillay

I like to add a bit more to Gnd Kumarans answer.
INCLUDE LOAD CURRENT, LENGTH,VOLT DROP AND
1)Type of cable cu/ al, underground, pvc etc
2}how you want to lay eg overhead line, conduit,
underground. cable tray, trunking.
3)if necessary type of protection you are giving
than with the help of the manufacturers cable catalogue you
can safely determine the cable size.
there is no fast rule to say cu cables carry 2.;5 times &al
cables carry 1.5 times the cable size to determine the cable
size.

Is This Answer Correct ?    0 Yes 0 No

How do you select a cable size(cu and Al) for a particular load..

Answer / rsbangra

cupper cable take 2.5 times current its ratting in mm2
and aluminiuam cable taken 1.5 times of its ratting.

exampl. 10 mm2 alu. cable take 15 amp current
and cupper cable 10 mm2 cable take 25-30 amp.

Is This Answer Correct ?    1 Yes 3 No

How do you select a cable size(cu and Al) for a particular load..

Answer / mohit.k.k

it depends upon length. but you can take it as for al cable
1 sqmm = 1a and for cu 1sqmm = 2.5 a

Is This Answer Correct ?    7 Yes 10 No

Post New Answer

More Electrical Engineering Interview Questions

Why we use 2core cable for Dc motor.Can I use 3core?

5 Answers   JK Paper, Maharaja Whiteline,


what is meant by trivector meter?

2 Answers  


How npn and pnp transistor works

0 Answers  


what kelvin's law ?

0 Answers  


Natural frequency in the control system represents nature of a. Transient response b. Oscillations c. Overshoot d. Speed of responce

1 Answers  


How Earthing is prevents shock?Explain

4 Answers  


what is overflexing in transformer? setting?

1 Answers  


How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?

1 Answers   NTPC,


What is Minimum permicible meggering value for following 1) LT Panels (Ph to Ph / Ph to Earth) 2) 11 KV, HT Panels (Ph to Ph / Ph to Earth) 3) 11 KV Cable 4) LT Cable

1 Answers   BFL,


explain with the help of loading capability curve,reactive power generation and absorption from synchronous generator?

0 Answers  


what do you mean by leading power factor & lagging power factor

13 Answers   Suzlon,


why we grounding the neutral of a transformer?

3 Answers   GAS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)