The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / bikash

SImple earth is always in zero potential, so when u connect
neutral to earth or measure voltage it will show zero
voltage. But actually neutral is the return path or it is
required for completing a ckt. It shows the unbalaced
system voltage. If system is balaced neutral will show zero
voltage or otherwise it will show voltage. So check load
condition.

Is This Answer Correct ?    6 Yes 1 No

The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / m.mousa

Hi Ravi
Of course if you have your power supply neutral earthed
from supply side (transformer or generator neutral) you
will get zero potential at between the neutral and earth at
any point of the distribution circuit ; you should get more
information about the type of your earthing system (IT, TT,
TN-S or TNC)
You can find more details at Schneider site or ABB sites
or directly from IEC 60364-5-54 Electrical installations of
buildings - Selection and erection of electrical equipment -
Earthing arrangements

Is This Answer Correct ?    2 Yes 0 No

The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / ravi mittal

The problem has been solved now. I have installed an isolation transformer
which has solved all the issues.

Is This Answer Correct ?    2 Yes 0 No

The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / ravi mittal

Dear Bikash,

I am thankful to you for taking interest in answering my
query.

Actually, I have an equipment for which I have been clearly
indicated to not have neautal and earth shorted. If done
so, the equipment may have problems in future. When we
check with the multimeter the neautral to earth is showing
as shorted which gives a zero reading which is actually not
shorted. What can I do in this case where can I either get
a 0 reading (when not short) or <3 volts reading? Is there
a fault with my wiring? Some electricians say that this is
a usual phenomenon in industrial areas. If the phenomenon
is usual, is there a device which can be installed to
rectify this problem.

Thanks and regards,

Ravi Mittal

Is This Answer Correct ?    1 Yes 0 No

The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / kannan

Cheech your earth value as per standard. If not install new
earth rod. It may solve your problem.

Is This Answer Correct ?    2 Yes 2 No

The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machi..

Answer / nadir

Possibly your machine required an IT wiring which is unearth neutral. Your machine may required only a PE and the PE electrode shall be installed at a distance of 1.5 longer than your transformer/ neutral earth electrode length.

The isolation transformer will also create harmonics and required to dissipate.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

WHAT IS THE DIFFERENCE B/W BUSHINGS AND INSULATORS? WHAT IS THE CREEPAGE DISTANCE ?

3 Answers   TCS,


In a panel 2500A ACB is the incoming breaker then what is the size of the bus bar?

1 Answers  


State kirchoff voltage law?

0 Answers  


why the voltage transmission is always in a multiple of 11? e.g. 110 V, 220 V, 33 kVA, 11 kVA

16 Answers   IAF, MahaGenco,


when 40 watts and 60 watts bulb is connected in series, which bulb glows brightly ?

5 Answers  






why capacitive load is not used in routine life????any reason is there ??????

0 Answers  


Do you know the overhauling of a motor?

12 Answers   EdCET, Mecon,


why generator one end side star neutral point given? if this point not given what happen?

1 Answers  


what clearance required for 4.5 mva dry type transformer?

0 Answers   SPS,


What would be the ratio of a Delta-Wye tranformer having 48000 volts phase to phase on the primary and 4160 volts phase to phase on the secondary?

5 Answers  


WHEN SINGLE PHASE SUPPLY AS 220V, WHY THE 3 PHASE- 4 WIRE MEASURED AS 440 VOLTS INSTEAD OF 660 VOLTS (220 VOLTS PER PHASE i.e 220x3 = 660 volts ).

1 Answers  


Why LVDT have secondary windings connected in differential 1. Higher out put 2. Based on the out put voltage-/+, helps to identify the direction of displacement 3. To establish a null/ reference point

1 Answers   GATE, PSPCL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)