how to select cable size?
Answers were Sorted based on User's Feedback
Answer / itsme
1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation
design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!
if volt drop exceeds 9.2 volts use bigger cable
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / peer
If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.
I=100A (Apprx)
Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.
Is This Answer Correct ? | 20 Yes | 9 No |
Answer / vzvodator
See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / iftekhar mahmud
Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W
I would like to use 3 separate single core instead of using
3 core cable.
Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / vijay shinde
it simple it should be select on how much current will
cable carry
Is This Answer Correct ? | 6 Yes | 13 No |
Answer / ahmed bilal
for calculating cable load, you have to email me
aoabilal@gmail.com
Is This Answer Correct ? | 4 Yes | 17 No |
Answer / ashutosh tiwari
according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size
Is This Answer Correct ? | 14 Yes | 30 No |
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
What is on delay and off delay timers
what are the application of over current relay?
how many joint can done in HT line and what is life of the joint
0 Answers Micro Labs, Reliance,
3 shows a 415 V, 3-phase generator supplying a 3-phase 415/110 V transformer. Draw the individual and combined impedance diagrams to a base of 10 kVA. Determine the system fault kVA and the fault currents at the 415 V and 110 V busbars for short circuit faults on the transformer input or output terminals. Work in p.u. values of impedances.
What type of fittings and electrical accessories can be install in radiation area ?
What is the function of an exciter in a generator?
why electronic instruments is more favorable than electrical?
what is servo motor and how it works?
what is working parincipal of a ht transformer
At what condition differential relay will act in transformer and ht motor?
1 Kva = How many KW