what happens if generator is running leading power facotor?
Answers were Sorted based on User's Feedback
Answer / alee xain
If it is a Synchronous generator, then upon loss of
excitation it starts running at leading power factor. In
this case it would act as "Induction Generator", providing
active power to grid but taking reactive power from it.
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / sethar12
Generator will generate active power (compulsory?) and
leading reactive power. Heating effects of magnetic field
will be both on generator rotor and stator. Generator
terminal voltage increases from its rated voltage. Generator
(and grid) tripping may occur if the inductive load demand
from grid suddenly increases and generator AVR is in manual
mode (as is a normal practice).
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / deepak
in leading power factor circulating current flow in stator
& stator end ring will damage
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / suthan prabhu
If the generator is running with leading powerfactor ,Power
Utilisation is more than the power generation.
| Is This Answer Correct ? | 2 Yes | 11 No |
Answer / gi
losses decrease,the genterated power(kva) decrease.
| Is This Answer Correct ? | 5 Yes | 16 No |
Answer / pandi
if generator run at leading power factor means it supply
the reactive power
| Is This Answer Correct ? | 3 Yes | 14 No |
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
How calculated single phase induction motor req. Capacitor?
what will happen if a part of primary winding of a transformer is accidentally short-circuited?
what is the advantage of NiCd battery over Lead acid battery?
220/33kv voltage level having 60MVA rating , which transformer is preferred two winding or auto transformer. why, kindly provide your strong technical valuable views.
what is meant by tranformer impedance?
Petroleum jelly is applied to the terminals of the lead acid battery is to prevent?
what is ferranti effect?
HOW TO CONNECT THREE PHASE OVER LOAD RELAY FOR SINGLE PHASE
Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.
Can anyone tell me what will happen if AC & DC supply get mixed???
I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)