what happens if generator is running leading power facotor?
Answers were Sorted based on User's Feedback
Answer / alee xain
If it is a Synchronous generator, then upon loss of
excitation it starts running at leading power factor. In
this case it would act as "Induction Generator", providing
active power to grid but taking reactive power from it.
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / sethar12
Generator will generate active power (compulsory?) and
leading reactive power. Heating effects of magnetic field
will be both on generator rotor and stator. Generator
terminal voltage increases from its rated voltage. Generator
(and grid) tripping may occur if the inductive load demand
from grid suddenly increases and generator AVR is in manual
mode (as is a normal practice).
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / deepak
in leading power factor circulating current flow in stator
& stator end ring will damage
Is This Answer Correct ? | 2 Yes | 11 No |
Answer / suthan prabhu
If the generator is running with leading powerfactor ,Power
Utilisation is more than the power generation.
Is This Answer Correct ? | 2 Yes | 11 No |
Answer / gi
losses decrease,the genterated power(kva) decrease.
Is This Answer Correct ? | 5 Yes | 16 No |
Answer / pandi
if generator run at leading power factor means it supply
the reactive power
Is This Answer Correct ? | 3 Yes | 14 No |
How to calculate impedance volt in Transformer?
Why auxiliary transformers are not connected in parallel in primary stations?
Why we are not using capacitor in line when load on Genset?
am commissioning the trafo without connecting the neutral therefore unbalance will occur what is the alternative solution for this?
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.
checklist of ELCB
what are the method of testing of transformer??
How to calculate the TR (AC's)
How to convert from HP to BHP please explain????????
can any one suggest me the tilt angle of my solar pannel ?? or tell me how can i know the fix tilt angle of my solar pannel?? my cordinates are 31.503629,72.993164.
what is different between relay and plc?
how to check a transformer insulation?
3 Answers Kirloskar, Kirloskar Chillers,