Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what happens if generator is running leading power facotor?

Answers were Sorted based on User's Feedback



what happens if generator is running leading power facotor?..

Answer / alee xain

If it is a Synchronous generator, then upon loss of
excitation it starts running at leading power factor. In
this case it would act as "Induction Generator", providing
active power to grid but taking reactive power from it.

Is This Answer Correct ?    23 Yes 5 No

what happens if generator is running leading power facotor?..

Answer / shahin

If the generator is running with leading powerfactor , the
generator's generated voltage will increase.....

Ref. Puschein & Loyd book.

Is This Answer Correct ?    10 Yes 1 No

what happens if generator is running leading power facotor?..

Answer / sethar12

Generator will generate active power (compulsory?) and
leading reactive power. Heating effects of magnetic field
will be both on generator rotor and stator. Generator
terminal voltage increases from its rated voltage. Generator
(and grid) tripping may occur if the inductive load demand
from grid suddenly increases and generator AVR is in manual
mode (as is a normal practice).

Is This Answer Correct ?    2 Yes 1 No

what happens if generator is running leading power facotor?..

Answer / anil

alee xain answer is correct

Is This Answer Correct ?    1 Yes 4 No

what happens if generator is running leading power facotor?..

Answer / gi

it will ac as synchonous generator

Is This Answer Correct ?    5 Yes 11 No

what happens if generator is running leading power facotor?..

Answer / deepak

in leading power factor circulating current flow in stator
& stator end ring will damage

Is This Answer Correct ?    2 Yes 11 No

what happens if generator is running leading power facotor?..

Answer / suthan prabhu

If the generator is running with leading powerfactor ,Power
Utilisation is more than the power generation.

Is This Answer Correct ?    2 Yes 11 No

what happens if generator is running leading power facotor?..

Answer / gi

losses decrease,the genterated power(kva) decrease.

Is This Answer Correct ?    5 Yes 16 No

what happens if generator is running leading power facotor?..

Answer / pandi

if generator run at leading power factor means it supply
the reactive power

Is This Answer Correct ?    3 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes

0 Answers  


How calculated single phase induction motor req. Capacitor?

0 Answers  


what will happen if a part of primary winding of a transformer is accidentally short-circuited?

2 Answers  


what is the advantage of NiCd battery over Lead acid battery?

1 Answers  


220/33kv voltage level having 60MVA rating , which transformer is preferred two winding or auto transformer. why, kindly provide your strong technical valuable views.

1 Answers  


what is meant by tranformer impedance?

0 Answers   Synergy,


Petroleum jelly is applied to the terminals of the lead acid battery is to prevent?

2 Answers   KSEB,


what is ferranti effect?

9 Answers  


HOW TO CONNECT THREE PHASE OVER LOAD RELAY FOR SINGLE PHASE

2 Answers   Quest,


Multimeter show phase to neutral volt 230 the per phase but phase to phase 415 not show 460 why.

1 Answers   Intas,


Can anyone tell me what will happen if AC & DC supply get mixed???

9 Answers  


I'm looking for a mnaual set for a Teradyne J750. Softcopy would be preferred but I'll take what I can get.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)