Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N.B transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA CHANDRS PANDA
Mob No. 9437917849
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / santosh bangar
rating of any electrical equipment its depends on how much heating ( by losses) is permissible.
in Transformer , rated output limited by heating and hence by the losses in the transformer
two types of losses in transformer Copper loss( proportional to I) and core loss proportional to V)
we have constant power VI in transformer
if we increase Voltage then current will reduce
and if we increase current then voltage will reduce
we can not go beyond certain limit of voltage ... limited by core loss
and also can not go beyond certain limit of Current..limited by copper loss
means we know what is max voltage and max current and VI is rating of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
Why are we not getting shock while touching a metal which is being welded?
The series field winding has low resistance while the shunt field winding has high resistance. Why?
Which is capital of Indian State Tripura ?
What about electrical Units. discrive in detail
How can two 3 phase transformers of same KVA and Voltage be connected in parallel?
0 Answers Bernhard Schulte Shipmanagement,
What is short circuit analysis of electrical networks?What are the procedures to be followed for its calculation?
in soft starter system for 375 KW 3 ph induction motor for multi stage vertical pump, two thyristers failed causing shorting of thyrister. the motor winding failed while starting.What is the cause and what is the effect in above case
what is the impedence
Sir, how to calculate the voltage drop and short circuit current of cable. please give me example and formulas.
what is diffrent between plc and clc??
Please let me know when replacing electromechanical Relays for protection of generators with sr489 multilin Relay, then there is no need to use 86 master trip relay Too. I am wondering this multilin relay has no contact to Stop breaker reclosing as 86 does
Min and max capacities of VCB,ACB,ACCB,OCB,MCCB and MCB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)