how many ht 11 kv cable size for 11kv 2000 kva 11kv*433v transformer ?
Answers were Sorted based on User's Feedback
Answer / prashant soni
HT Cable size dependson fault level to be withstood and its duration..
If you take XLPE, HT Cable of ALU conductor,
condiering 350MVA for 1 sec *(18.37kA), min. C/A will be found out by Area(A) = (Short ckt current (kA)*Square root of Time)/k
k is constant = 0.094 for XLPE ALu conductor.
This will give you min. size required for HT system (11/22/33/6.6/3.3kV)
Choose nearest standard higher size for HT Cable..
primary 3*240 sqmm AL cable
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ahmed
how many cable shoul be connected for 2000kva transformer of 11kv.
primary 3*240 sqmm AL cable
Secondry 4*630 sqmm AL / single phase (L1,L2,L3 & L4)
(u1,u2,u3 & u4) R-Phase
(v1,v2,v3 & v4) Y-Phase
(w1,w2,w3 & w4) B-Phase
(N1,N2,N3 & N4) Neutral
Is This Answer Correct ? | 2 Yes | 2 No |
How to connect the earthing in aircraft?
Diode is active or passive element?
why do we not use equivalent voltage source in negative sequence equivalent ckt.
Can we use 11kv Trivector Metre or Energy metre instead 33kv Metre at 33kv Over Head Line metering purpose?
how the capacitor work on dc?
why generator is design for lagging P.F(power factor)?
How much load with stand the copper cable by sq mm apro..
How to calculate Number of Earthing Pits....???
In dc ckt. 24v or 110v, which one is more efficient and why?
can anyone show me how the 3 phase power is supplied to socket outlets?
why we use RYB phase sequence? and somewhere we use UVW ? why?
6 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited, MUET, TCS,
why earth hole size is biggest in plug point?
22 Answers Al Qabas, HCL, RRB,