we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
Answer / chanchal
at first check the air supply.if it is ok then
feed the 4mA by using calibrator in i/p converter of positioner. if valve is zero position(fully closed) then its ok.if valve is not in zero position(fully closed) then set the zero position in positioner by using zero point screw.
next feed the 20mA by using calibrator in i/p converter of positioner.if valve is 100% open then its ok.if valve is not 100% open. then adjust the span setting by using span screwin positioner.
then check 25%,50%,and 75% open position in valve by feeding 8mA,12mA,and 16mA by using calibrator in same way.
Is This Answer Correct ? | 4 Yes | 5 No |
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.
Is it ok, to use non-contact type Radar type LT, on a tank that is half circular from the bottom side? If yes the, isn't the waves gonna bent in other directions?
0 Answers Process Control Technologies,
.how does CSADA systems display the process variable value?
how to check the leak in thermowells
what is flow
how the 2.5bar pressure able to control the 40bar steam
8 Answers IBM, PAFL, Thirumalai Chemicals,
what is loop?
what is the difference between single and double compression cable gland
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
What is the purpose of valve positioner. Explain 4 uses.
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
i have height of stem drum level 1000mm.how i calculate the DP transmitter