1.What is wind span ,wight span and normal span, and what is the difference for 132kv transmission .
*The wind span is that on which the wind is assumed to act transversely on the conductors and is taken as half the sum of the two spans, adjacent to the support.In order to take full advantage of towers located on elevated ground, it is usual to allow a wind span of 10 to 15 percent in excess of
the normal span. This additional strength can be used in taking a samll angle of deviation on an intermediate tower, where the actual wind span is less than the design wind span. The angle of deviation to be taken in such cases is approximately given by:
θ =( wl /π T )x x180
Where w = total ind load per unit run of span length of all conductor
carried by the tower,
l = difference between the wind span used for design and the actual
wind span, and
T = the total maximum working tension of all conductors carried by the
tower.
*The weight span is the horizontal distance between the lowest point of the conductors, on the two spans adjacent to the tower . The lowest point is defined as the point at which the tangent to the sag curve, or to the sag curve produced, is horizontal. The weight span is used in the design of cross-arms.
Is This Answer Correct ? | 3 Yes | 0 No |
The neutral to earth connection in my industry is showing a zero reading (shorted). I have a machine which has to be installed where neutral to earth is not shorted and shows a leak voltage <3 Volts. Please suggest me how it is possible.
Iam Preparing For Ap Transco Assistant Engineer (ELECTRICAL) Exam how To Prepare What Is The Refernce Books.can You Give The Advises To Me.tahnk You. This Is Radhika Iam Preparing For Ap Transco Assistant Engineer (ELECTRICAL
Even when a particular generator in a generating station is under maintenance we are still able to maintain the same power output. How is this possible? Does the tie line between 2 generating stations have a role to play in it?
what is diff between Ground/Earth & Neutral?
Tell me all plants load factors i.e which plant operating on which load?
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
How Kneepoint voltage of CT practically related when CT in service. ie Knp is above 670 what exactly means
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
why Lightening Arrester Probe sharp at Top of telecom tower.
1 Sq.mm ( Aluminium Cable ) = How much Amphere ( AMP )
Why delta connected motors are used normally.
all 3 current transformers (C.T) are burnt in a L.T Panel - what are the possible reasons