Answer / kingshuk dey
To start with, let's get our concepts correct. The motor supply comes from the VFD, which in turn is connected to the power supply from a board (or LT side of transformer, in your case).
Supply(TRF) --> VFD --> Motor
First off lets assume your VFD type is less than or equal to this LT supply. (LT/HT for TRF is subjective, Lt can be 220V when HT is 460V, or 460V when HT is 1000V etc). But a 460V VFD will burn its fuses if connected to 1000V.
Anyway, if you connect the VFD to LT side, and the motor is HT (meaning it's rated for a heavy current like 32KV), the motor will try to pull more and more current to start from the VFD, ultimately exceeding the current setting of the VFD and it will trip with an Overload or Overcurrent (OH, OC) fault on its display. If the current is enough to start the motor, it will rotate, but with very less speed (like if the motor is not connected to any load).
Just as a matter of interest, if you connect the LT side of TRF to VFD, and HT side of TRF to motor, "nothing" will happen as there is no current source (both VFD and motor are current consuming equipments) :P
Motor --> TRF HT -- TRF LT --> VFD (LOL!)
Is This Answer Correct ? | 1 Yes | 3 No |
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
How a generator is positioned in a hydroelectric power plant?
power generation unit kw/hr or kw/day ?? please answer me engr_kalam@yahoo.com
How to increase the specific gravity of DG batteries?
why overcurrent fault occurs in power system.
800a siemens vcb in our company can not be closed electrcally an mechanicaly cc and oc coils are found ok. why?
why PT Primary are the grounded?
which type of stability limit is higher,steady state or transient? why?
what are the advantages by using IGBT in VSC HVDC than thyristor in conventional HVDC
Types of tempering of energy meter?
WHY AIR COMPRESOR IS STARTED UNLOADED
can we install HT panel & LT panel side by side or how much clearance is required ?