How to calculate flow of air bubbler type level transmiter
According hight and density
Answers were Sorted based on User's Feedback
Question: How to calculate flow of air bubbler type level transmiter? According hight and density?
I love this question because it deals with the understanding of how a bubbler works - flow is not the issue, pressure is.
The calculated value for a bubbler is NOT flow. The critical, calculated value for a bubbler is pressure, because the air/gas pressure in the bubbler tube is a direct representation of the head pressure of the liquid column; which in turn, can be interpreted as the level of the liquid column.
Measurements of head pressure are always done in units of water column (wc), inches of water column or mm of water column, because water column is universal everywhere in the world.
The column of liquid might not be water, it might be some chemical or solution whose specific gravity (density) is not the same as water. So to determine the level, the head pressure measurement of the air/gas pressure in the bubbler dip tube needs to be corrected by the specific gravity. Level = measurement (wc)/specific gravity
The flow rate of air/gas is typically just enough to create a constant stream of bubbles, proving that the air/gas column in the tube has sufficient pressure to overcome the liquid column head pressure. Flow rates regulated by a constant flow, differential relay range from 0.5-2.0 CFH (15 L/hr to 55 L/hr).
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / madani
Suppose level to be measured is 02 meters from the datum line.Fill the vessel with service liquid of 02 meters
height and adjust the purge rotameter flow until Transmitter output reads 20 ma DC.
Is This Answer Correct ? | 0 Yes | 2 No |
why we use -ve voltages in vibration prob?
what is seebeck effect?
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
What is the right procedure for adjusting the gap voltage of bently nevada vibration sensor?
What is diffrent profibus & OFC Communication
Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?
what is the difference between transmitter and smart transmitter ?
What is the difference between working pressure and calibration pressure of a control valve
Draw a 3 element level control loop and explain
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.
if field commnictor 475 does not communicate with transmitter what will you do ?
while i check zero check for dp flow transmitter some fluctuating came (0 to 458 kg/h) what is the reason?