Answer / ahmallam
RTD Sensor can't be calibrate , you can only calibrate the transmitter only by potentiometer according to PT100, PT1000, ...... table.
or you can use comparison calibration.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / carl_ellis
An RTD is 'calibrated' by heating or cooling it to various
temperatures, measuring its resistance at those
temperatures, and the recording and analyzing the measurment
results.
An RTD's performance can not be adjusted like a temperature
transmitter's output can be adjusted, but its performance
can indeed be measured in a periodic calibration.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ajay kumar gupta
An RTD is 'calibrated' with the help of Temp. bath by selecting required temprature. You can compare RTD resistance, RTD Chart accordind to type RTD. There is no adjustment in RTD.
Before installation RTD in field this checking is must.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / yugesh shah
Calibration of rtd is not possible , yeah just know about error is possible when other rtd same type using in same place ..
| Is This Answer Correct ? | 0 Yes | 0 No |
what is different betwen Process zero and atm zero?
what are the inputs (drawings) we need to prepare loop schematics??
How to find out the current of two motors having same power consumption but different RPM?
Is there any interfacing sofware to build communication between a PC and ER300P model L&T make trivector meter via RS485 port which is available in the meter and is there any data acquisition card available to store the acquired data from the meter into the system
Dear friends, I have a question: We work on a project which has some boilers to provide steam for desalination unit. The boiler area is safe and the only hazard source is the fuel lines of boilers. I want to know according to NFPA standard which type of instrument should be selected on the fuel line: Eex Type or Non-Eex type? Thanks in advance
how will you segregate the alarm levels in alarm management system during factory Acceptance Test
how to calibrate electro pneumatic positioner 8013 mil controls ltd ?gsr
what pressure transmitter?
How to define the size of control valve?
Displace type LT to be calibrated in workshop, wt. 40, dia- 60 mm, density- 0.8kg/cm3.
I m appointed as an automation trainee engineer in small firm in that I am only the one , my company give me a project on s7-200 as i m beginner I don't know how to program so please send me the helpful site so that I complete my project before deadline....please help me out in this critical situation.
1 > HOW TO MEASURE INTERFACE LEVEL 2 > DIFFERENCE BETWEEN RADAR & ULTRASONIC LEVEL TRANSMITTER
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)