If I installed wrong directions orifice plate then what showing
value d.p transmitter?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Various published papers (from USA's Nuclear Regulatory
Commission to Gas Technology Institute) agree that an
orifice plate installed backwards reads low anywhere from
8-25% below the actual true flow rate.
Furthermore, under-measurement error is reasonably well
correlated by the orifice "Beta ratio".
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 1 No |
WHAT IS SMART SENSOR AND DIFFERENT B/W SMART SENSOR AND SENSOR??? PLS GIVE ME ANSWER AS SOON AS POSSIBLE.....
In RS 500 SLC 5/03 input change one module card to another card, plz. give steps clearly.
why magnetic flow meter is not used in thermel power plant operation
Why we are using DPT(Differential Pressure Transmitter) in separator instead of level trasmitter?
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???
what is your eligibility criteria for freashers?
how to calibrate pressure gauge(we can not able to fixed by pointer screw adjustment and pointer re fixing method)
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
What is transducer
If I want to buy a pressure switch & 3-way valve for hot water application then witch parameter I should consider.
two common seiling liquid used in seal pots are:
What is the purpose of valve positioner. Explain 4 uses.