Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???

Answers were Sorted based on User's Feedback



We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC ..

Answer / carl ellis

Although the post has lots of information, it isn't clear
exactly what the problem is.

I think the problem is that the PLC does not alarm when the
pressure exceeds (goes above) 55mbar. But I'm not sure.

Given this description: when PAHH (pressure alarm High High)
goes more than the set point which is 55 it reached up to 71
but due to timer doesn't trip . We force it and we checked
everything nothing there, let's suppose that the PLC is not
indicating an alarm state.

a) what should the PLC do at the alarm condition?
b) How is an alarm indicated? A digital output (DO) goes
high? A lamp is driven by a DO lights up?
c) What exactly does not work as it should?

If the PLC does not indicate an alarm, yet the indicated
pressure goes higher than a high alarm, the problem is NOT
the field transmitter, the problem is in the alarm setup or
alarm annunciation.

Troubleshooting depends on
- an explanation of exactly what should be happening
- an explanation of how you know it is not working; that is,
what the evidence is that it is not working.

Yes, the pressure went above 55mbar.
How do you know that?
The transmitter's local display?
A milliampmeter in the analog input circuit?

Did the alarm ever work? Or is this a new commissioning and
you're trying to get the alarm to work?

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC ..

Answer / jigar anadkat

Dear,

As you mentioned pressure shot up to 71 mBar which means channel goes to BAD state and it might not activate the logic. (Truly speaking it should but depends on how the logic has been created and what are the parameters set in IO assignment for failure situation).

If you you are using Yokogawa Prosafe RS the please make sure to take Chanel status as well in the logic configuration. So in case of IOP(+) as well as IOP(-) it will actuate the logic.

Moreover, there is a setting in IO parameter builder regarding input processing at fault situation. Please go through that as well.

Hope this will help you in trouble shooting.

Regards,
Jigar Anadkat
Instrument Engieer
IBN RUSHD
A SABIC affeliate.

Is This Answer Correct ?    1 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

What is the procedure of mounting new positioner on pneumatic control valve?

1 Answers  


What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?

0 Answers   Process Control Technologies,


in DCS or PLC we can not put all ai or di,there is calculation through which we can accomodate certain no of digital and analog signal.I need to know that calculation

1 Answers  


how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).

4 Answers   TATA,


kindly sent some demo question and answer

0 Answers   HPCL,


What is trim material . Why it is known as trim.

1 Answers   L&T, LNG,


A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.

0 Answers   MNC,


WHAT IS THE DIFF BETWEEN FREQUENCY AND INTENSITY?HOW IT WORKS IN FLAME SCANNER ?

1 Answers  


Could you explain to me the enraf (servo gauge) mechanism. How it works ? and how it is working on archimedes theory while it's not immersed into the surface? and how can we calibrate it ? Thanx

1 Answers  


What is the DIfferences between SMART transmitters and PROFIBUS DP/PA Transmitters?

4 Answers  


what is difference between Floating D.C.Voltage and Fixed D.C.Voltage?

2 Answers  


what is principal of pressure transmitter?

5 Answers   Hindalco, SPB,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)