i am confused about generator.
i have generator of 380 KVA that is 304 KW by that formula
KW=KVA*0.8...
then by this formula I=KW/V*1.732*0.8 the amperes are 528.673.
so that is the load which i put on one phase of generator or
this is total 3 phase load on Generator.......
Answers were Sorted based on User's Feedback
Answer / sheikh
in single phase distribution system every one phase have to
bear 528Amp with neutral. in 3phase distribution system the
sum of current with phase to phase will be 528amps.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
in usage of single phase supply every one phase have to given
528 amperes . in 3 phase distribution the sum of current
will be same as 528 amps.
Is This Answer Correct ? | 0 Yes | 0 No |
Thanx alot sheikh... :)
but still one thing i ask u to plz tell me.....
if we run 3phase motors at this generator then maximun load
on generator is 528??
and if yes then we can say that the load on one phase is
528/3=176 amp ???
one more thing plz tell me the maximum load of generator 400
KV.A if we use it for 3phase motors...voltage 400v...
this load plz tell me in amps and also in watts....plzz its
urgentt plzzzz mann....i will be thankfull to u :)
Is This Answer Correct ? | 0 Yes | 0 No |
whatis mean by voltage?
What is the operating range(tolerance) of voltage and frequency of grid supply in india?
why maintain the Dg PF is 0.8? Explain?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
what is AVR and tell principle and working?
10 Answers ITC Infotech, MIOT Hospitals, YCC,
friends., why celling fan rotate cockwise direction and wall fan anticickwise direction ?
The control system is used for?
explain why the secondary terminal of current transformer should not be lift open circuited.
Can 2 nos. of 1 ton split ac be used through a 20 am supply meter?
Can we use 230VAC, 63A MCB for 120VAC, 63A supplied heaters load?
Explain mechanical rotational system?
Can we inject more current in ct primary paralleling 2 loading transformers/Injection kit at a time?let ct ratio be (5000/1A)(per kit rating 2000A range),i need to inject 5000A,if this cant b done means wat is d optional?