can i calibrate DP transmitter online (while Tx in Service)
if yes ,how?
Answer / carl_ellis
In order to 'wet'calibrate a transmitter (by applying
reference pressure), the transmitter needs to be powered,
but if the transmitter's output signal is an input to a
control loop or alarm, then those functions need to be
disabled (loop put in manual, alarm disabled) because the
transmitter's output is not representative of the process
during calibration.
The transmitter has to be isolated from the process, so that
cal pressure can be applied. This done through isolation
valving; typically a 3 or 5 valve manifold for a DP transmitter.
So, is a transmitter 'in service' if it's powered, but its
signal is not representative of the process and is, in fact,
isolated from the process?
My answer is no, a transmitter being calibrated is not 'in
service'.
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
what is Dry Leg calibration and where is it used
explain key exchanges in all security modes WPA,WPA2,TLS?
Explain the use of hair spring in the pressure gauge.
What is Integral and Derivative control?
hiii.... can any one provide me previous years question paper of hindustan petroleum for instrumentation engineering???
ON RADAR INTERFACE LEVEL TRANSMITTER IF DI-ELECRIC IS WRONG WITH CONTINIUS PROCESS THAN HOW CAN INDENTIFY OR HOW CAN I PUT NEW DI-ELECTRIC VALUE?(ROSEMOUNT-TDR-3300-COXIAL PROBE TYPE)
what the differant between Wet Leg /Dry Leg
how many types of spped sensors n vibration sensors?their basic principle n connection?
how to know the URL and LRL for steam drum level and why the calibration range is in negative ?
while stroke checking of a linear control valve ,found its travel is in non linear ,what can be possible reason ? ( please answer send in mannanali65@gmail.com) pls pls pls if any body know
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
In VVVF DRIVES VOLTAGE IS ALSO VARY WITH THE FREQUENCY. HOW? WHAT IS THE DIRECT FORMULA RELATING THESE TWO.