can i calibrate DP transmitter online (while Tx in Service)
if yes ,how?
Answer / carl_ellis
In order to 'wet'calibrate a transmitter (by applying
reference pressure), the transmitter needs to be powered,
but if the transmitter's output signal is an input to a
control loop or alarm, then those functions need to be
disabled (loop put in manual, alarm disabled) because the
transmitter's output is not representative of the process
during calibration.
The transmitter has to be isolated from the process, so that
cal pressure can be applied. This done through isolation
valving; typically a 3 or 5 valve manifold for a DP transmitter.
So, is a transmitter 'in service' if it's powered, but its
signal is not representative of the process and is, in fact,
isolated from the process?
My answer is no, a transmitter being calibrated is not 'in
service'.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
What output voltage the proximity switch shows when it is in open enviornment?
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
what is the meaning of Domain server?
what is the importance of CV in the control valves? how it is calculated?
What are the different modes of a contollogix family processor? How they work?
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
what is earthing ,grounding in c&i panel?what is the resistance in earthing and grounding of c&i panel?what do u mean by shielding and what is its resistance?
what is the relation between flow and pressure.for example relationship between level and pressure is p = phg like that i want ans for this question.and also how to calculate orifice sizing and flow transmitter. pls some one ans for this questions.
In my company plc based winders are operated. one day there was a data transmission failure alarm shown on pc. as per sir instruction we have reset master plc but winders were not triped and alarm gone. so what master plc do?
Please tell me details about Sox,Nox,SWAS analyser????
how to relay switch sense the fault?
What is the difference between DCS and SCADA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)