In EHV transmission line a neutral grounding reactor is
often placed at neutral point of shunt reactors. What is
the recommended protection for this neutral grounding
reactor? Should I use a fast closing switch to bypass
neutral grounding reactor when this protection operates?
No Answer is Posted For this Question
Be the First to Post Answer
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
why plc need seprate earthing?
tate and explain super position theorem
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
we use capister for power factor. when we use capaciter in dg circuit than defect dg. can we use capaciter bank for dg circuit
How to increase the kvah ?
why we cant control neutral instead of phase in single phase?
BRIEFLY EXPLAIN THE STORAGE CLASSES AND THEIR TYPES IN C
What is difference between PVC cable & XLPE cable?
WHAT IS MEANT BY BTU OF AIR CONDITIONERS.
if acapacitor connected to power supply will it cosume power& will it going to get recorded in energy meter
Explain the laying procedure and laying depth of submarine/subsea power cable for 220/400KV system? Also available cable diameter?