I want condensate pots vent position erection of flow
transmitter ?
Answer / carl_ellis
A 'vent' or 'fill port' is installed at the top of a
condensate pot, facing upwards, so the water can be poured
through the vent's opening to fill the impulse tubing/piping
and the condensate pot.
Carl Ellis
Measure First
Is This Answer Correct ? | 4 Yes | 0 No |