Answer / wareagle

If the meter is designed to use a 100/5 ct, it will receive
5 amps when the load is 100 amps. If the ct were a 600/5,
the meter would receive only 1/6 x 5 amps or 0.83 amps
which would be a low reading. You would need to multiply
the reading by 6 to get the correct value. You would likely
not get the the exact reading with the 600/5.

Is This Answer Correct ?    3 Yes 0 No

if i conncet ct with ct ratio of 600/5 to an energy meter having ct ratio of 100/5, the reading sh..

Answer / pillay

the reading would be incorrect. you can multiply the reading
by 6.to get correct reading.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?

9 Answers   Wipro,


how to select electronic timer(Star-Delta) setting for diff. rating motors

0 Answers   Getrag Ford Transmissions,


what is the difference between arc and spark

2 Answers   ABB, Jindal,


we use capister for power factor. when we use capaciter in dg circuit  than defect dg. can we use capaciter bank for dg circuit

0 Answers   Syncom,


How many earthing pits required for diesel generator set ? Why ?

1 Answers  






what is the meaning of bus bar, in electrical panels.

13 Answers   HLG Habtoor Leighton Group,


What is the make of breakers, transformers, generators? What are their capacities and ratings?

4 Answers   Bharat Bijlee, GHPPL, Tata Motors,


How many kw will suply from one db

0 Answers  


what is the different between bus section and bus coupler

1 Answers  


Why we use Fuse in transformer in secondary side.Why we dont use fuse in primary side?

1 Answers   Care,


What is Partial Discharge test .Please specify that this test can be test on 11/0.433 KV,630 KVA Transformer.

1 Answers   NBCC,


say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)