Answer / pradyumna chandra panda

For 11kv suppy it is 40kv/2mm at normal temprature is ok. As per my experience it is reach upto 125kv/2mm at 40°c after filtration but we keep it 60kv/2mm NB-Below 24kv/2mm is rejected oil.

Is This Answer Correct ?    6 Yes 1 No

What should be the BDV value of a new transformer oil..

Answer / koti

As per IS : 335-1993, it is 30 KV(unfiltered)
and 60 KV(After filtration).

Is This Answer Correct ?    2 Yes 0 No

What should be the BDV value of a new transformer oil..

Answer / @arena

75kV/mm

Is This Answer Correct ?    2 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

100 MVA 3-phase alternator with earthed neutral has a reactance of 5 ohms per phase. what will be the fault MVA of generator.

0 Answers  


How calculate the Transformer Impedence With Example

3 Answers  


can a rotating machine give the DC output without commutator? if yes, how? if no, why?

6 Answers   BARC,


i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.

0 Answers   SCM,


in basic 2 phase will short means tripping the power but spot welding 2 phase shorting but not tripping it will welded why.....(Q)

0 Answers  






how many load we can take for lighting

0 Answers   ABB,


working principal of online ups

0 Answers   Delta Power Systems,


HOW TO CALCULATE THE CAPACITOR RANGE FOR LOAD FOR PF IMPROVEMENT? EXPLE:FOR 65 HP LOAD HOW TO CALCULATE CAPACITOR RANGE?

12 Answers   Al-Malik, All Star Electric, GEC, Reliance, Universal Industries,


Does the ELCB or RCCB trip when it is connected to a primary side of a welding transformer?

3 Answers   Tata Motors,


AMF (auto mains failure) control for DG sets at home.

1 Answers  


How the main bus bar rating of 400kV switchyard with one and half breaker scheme is calculated.

2 Answers  


why we maintain 50hz ,220volts,20Amp,ratings fixed every where in india,,electricity

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)