what are protective device needed to power a
360W ,50hz,240v,single phase,0.65 pf universal motor
Answer / suresh natarajan
Active Power: 360 Watts
Apparent Power:360/0.65=554 VA
Load Current 554/240=2.31 Amps
Protection Device should be 3-5 Amps.
Is This Answer Correct ? | 14 Yes | 1 No |