1)how many types of earth? 2)how many types of megger and how
to select that range? how much time taken for megger
calibration( we r using megger)
Answer / c.vadivel
Earthing of electrical machines are current are Bradly
classified in to current carrying earth and non current
carrying earth.
Current carrying earth:solid earthing,resistance
earthing,inductive earthing,grid type earthing and
capacitive earthing.
non Current carrying earth:making potential free metal part
associated to electrical machines and switch gears.
Megger are according to potential measurement classified as
low voltage megger ie 0 - 500V.,medium 0-1000V.,high voltage
megger 0-5kv,and 0-10kv
Is This Answer Correct ? | 6 Yes | 1 No |
can motors working at parallel operation like D.G set and transformers? It means asking about two motors coupled with same load???
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is the effect of impedance on the heat losses in case of AC system??? Does heat losses really depends on the impedance or depends only on resistive component only..??
What is PMG and AREP excitation system in generator
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
If cvt is most advance & effective(economically & stability)so why not use instead of VT(11 kv & 33 kv)?
15hp,380v,31amp,3-ph submersible motor run at 250v what is The temperature rise of submersible motor
generator(Deutz 550kv)is runing for 2 hours with load of 900 amp and then it goes in shutdown with alarm fault messege of speed fault although heirtz reading fixed at 50,what does that mean
differance b|w ground, neutral&earth
what are trouble functions of transformer?ex. prv trip,oltc,oti,wti.explain detail.
WILL THE PERCENTAGE IMPEDENCE FOR A ONAN TRANSFORMEER BE THE SAME COMPARED TO ONAF TRANSFORMER OF SAME RATING???
what is the internal working of star delta starter