What core magnetic balance test of transformer? How to do
this test in a three phase Star star (star-LV, star-HV)
transformer? How to measure and where to measure?
Answer / gautam patel
The Magnetic Balance test is conducted on Transformers to identify inter turn faults and magnetic imbalance.
Is This Answer Correct ? | 1 Yes | 0 No |
Differnce between earthing and nuetral
what is meant by loss of field in a DC motor? how a universal motor works?
what is the responsibilities of electrical project engineer?
why ac current do not save
detailed procedure how we calculate cost for pcc m10 and rcc m20 including centering and labour excluding steel/ iron
What is the de rating factor of cable? What is the importance of the de rating factor in cable selection?
Tan delta point in transformer to be earth or not?
AC current is flowing in a wire in your home how can you measure it(name of the instrument)
What is the purpose of shunt trip in ACB function?
what is different between installation and commonissonig.
Will it be OK to connect a 5MVA 33/6.6kV Ynd11 Transformer to a Star connected Motor. Or on other words connecting a Delta to a Star. I have another 30MVA 33/11 Dyn11 and would it be practical to convert it to Dd0 consequently converting the Voltage Ratio to 33/6.35kV Dd0.