can i use capillary type dp transmitter converted to
capillary type pressure transmitter. if i removed one side
capillary tube its work correctly?
Answer / k.sreenivasan
To begin with you must ask why there was a DP measurement
in the first place?
For example if you are measuring the DP across a Filter to
find filter choked condition, then removing one capillary
will defeat the basic concept.
If the DP xmr is used for a level measurement, then also
you will get wrong reading.
So unless you inform the details... correct answer cannot
be given.
By keeping one side of the transmitter open to atmosphere
by removing one capillary, the other side will read the
pressure with reference to atmosphere.
If you want vacumm pressure measurement then you have to
keep the HP side open and LP to the process. Vice versa for
gauge pressure measurement.
Is This Answer Correct ? | 3 Yes | 1 No |
in instrumentation why we are using 4-20mA , why not voltage ? if somebody design a instrument which works on voltage then can we use that instrument?
defffrence between instruments and instrumentation
WHAT IS THIS INSTRUMENTATION?
How to calculate P,I&D value in PID controller ?
0 Answers Jindal Steel and Power, SAL Steel Power,
What is meant by cold float of compressor shaft.
what is dry leg and wet leg in transmeter calibration?
How will you change the action of a control valve?
What is passive connection of instrument in different type of I/O module
principle of dead weight tester ?
meaning of SMART
PLS TELL ME THE FUNCTION OR PRINCIPLE OF CREEP RELEIF VALVE..
What is the logic a Transmitter control a Control Valve? How the signal going to the Control valve? What are systems/Panels/cables/signal used to control valve from Transmitter?