I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN
POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL.
1-IS BETTER WE USE CABLE?
2-IS BETTER WE USE BUS DUCT?
my transformer rate power is 2500KVA
Answer / mohamed
BETTER WE USE BUS DUCT BECAUSE :1-LOW VOLTAGE REACH TO 0
2- BUS DUCT WE HAVE BUS BAR WHICH CAN PROVIDED MORE CAURRENT
3-MORE FLEXIBILTITY
Is This Answer Correct ? | 3 Yes | 1 No |