If the on Of the DO module is off in the System cabinet,
then what is the Procedure to check weather the Module is
working or not.
Answers were Sorted based on User's Feedback
Answer / a k gunjariya
If DO Module is OFF in system cabinets:
1.) Check status of the 24 V Power Supply (power supply LED
on the module)
2.) IF No LED is glowing then module is not getting power
supply.
3.) if power supply led is glowing then check any of the
Digital Output signal by simulating input.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / ahmed samy
Make forcing from PLC programming software to any output Channel in that DO, if output is on, LED is on means module is ok, otherwise it's faulty.
Other idea, is to replace module with similar one in the rack, if it's still off in second position that means it has a problem
| Is This Answer Correct ? | 2 Yes | 0 No |
what is the importance of CV in the control valves? how it is calculated?
Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please
what is IEC code in cables & how to selecting cables?
Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Close on Fall Pressure Switch contacts are used. 2.If Pressure is abnormal as per set pressure,if connecting Terminal of pressure switch breaks,how the voltage extends to Relay base. 3.Are these contacts come under fail safe philasaphy.
how to calibrate the radar transmitter for measuring the exact tank level if tank is having agitator moving continiously because due to agitator tank surface level will vary every time.
what is a good line as ic engineer as maintenance ,oc, project, calibration ,validation engineer?
how to work static pressure sensore how to work dpt
whey we conect ammeter in series and voltmeter in parallel in circuit
what is radar type level transmitters and its basic principle and how to calibrate it
What is smart positionar
A flange is used for instrument connection for a system with a design temperature of 316C (600F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)