in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????
Answers were Sorted based on User's Feedback
Answer / tara shankar gupta
Any system desined is to optimam utilisation,here we have
to Xmr ie 100 MVA and 75 MVA, connected load is 155 MVA in
this case we cant optimize 75 MVA Xmr. in such situations i
will suggest Maximam loading of Big Xme and Load rest MVA
to smaller one.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / asm
first you have to confirm that 155MVA is connected or
diversified load, if it is connected load then 90% loading
is coming. however if it is diversified load then u can
load upto 80% of transformer capacity. in this case X'mer
will be out of higher efficiency range.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / santhosh
both the transformer is same rating it would be share equal
load,i.e (trafo1=2000kva,trafo2=2000kva),current load is
2200kva, now trafo1=1100,trafo2=1100
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The voltage drops in the transformers + line should be equal
at the secondary bus-bar. Current shared by tr1 x its %
impedance = load shared by tr2 x its % impedance.Hence The
load sharing ratio is inverse to ratio of % impedances.
Is This Answer Correct ? | 1 Yes | 0 No |
The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / harry
Higher Value Transformer u can Load upto 90% say 90MVA &
Lower Value Transformer u can load Load the Rest Say
remaining 10MVA.
It is General Practice to Do the Distribution of Load
According to above said manner
Is This Answer Correct ? | 1 Yes | 8 No |
what happen when we add mentos in cold drink?& why?
why the power factor of the induction motor is low?
DG Earth Value?
0 Answers Reckitt Benckiser, Vodafone,
For an 100kw generator, only 50kw of load is connected. will the generator generate only 50kw or 100kw. if it generate 100kw what happens to rest of the 50kw. what happens if we connect more than 100kw of load?
which of the following can produce maximum induced voltage..... (a)1amp dc current (b)50amp dc current (c) 1amp 60 cycle ac current (d)1amp 490 cycle ac current.
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
In track electrification Either we use single conductor or double conductor? why?
HOW MUCH CURRENT CAN A 3 -1/2 CORE 100 MM WIRE CARRY
what is the difference between 11kv and 13.8 kv? why we can't used one of these 2 sources?
Is current scalar or vector?
what is the function of compressor?
what is the IPC ? & what the uses ?