what do you mean by PF correction. A motor is rated at 15
kw,415 volts, 0.7 pf and eff of 0.92. The powerfactor is
improved to 0.98 by adding capacitors at the bus. calculate
the current drawn by motor under full load condition before
and after pf correction
Answers were Sorted based on User's Feedback
Answer / gk
Full load condition means rated power of 15 kw
condition.And P=VICOSQ. where v assumed to be maintained at
415v from terminal.So ICOSQ is constant to maintain rated
15kw(= (V)*(ICOSQ)) full load. Therefore if PF is improved,
current drawn by motor from supply mains will be reduced.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
You are connecting cap between motor and supply tapping
point. So, the first answer is correct . Current drawn by
motor and the feeder remains the same.There will be
reduction in current in the bus bar
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / lakshmi
pf correction means power factor improvement. for higher
factor the cutrrnt is reduced there by decresing the losses
and incresed efficiency occurs.
input power = output power / efficiency
I/p = 15000/0.92
= 16304.34 watts
I = p/ (1.732 * v * cos(phi))
= 16304.34/(1.732 * 415 * .7)
= 32.404 Amps before pf correction
I = 16304.34/(1.732 * 415 * 0.98)
= 23.416 Amps After pf correction
from the above values we said that the factor is improved
from 0.7 to 0.98 the current will be reduced from 32.404 A
to 23.146 A respectively.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / technicalarticlessbsvbsbsvb
No change. whatever was at rated pf will continue to be
drawn
Is This Answer Correct ? | 2 Yes | 5 No |
what is looping circuit in electrical lighting circuits?
State thevenintheorem?
why the field winding of synchronous machine is excited by dc source
Sir we have 12.5 MVA(110/11KV) transformer (Y-Y) connected,which tripped showing earth fault,when we charged transformer it stood OK ,but on connecting 11 KV feeders it tripped showing earth fault.our service engineers found that the B phase and R phase phase connecting to neutral broken from HV OLTC(on load tap changer),and R phase and Neutral is ok.Dissolved gas analysis shows that accetline content is high,tan delta value is 12.My dout is it is an internal fault of transformer,why REF or diffrential relay is not acted?
what is TPN
How to get Electrical Supervisory Licence in chennai Tamil Nadu from TNEB. I am BE EEE graduate.
What's difference between a400amps lt contactor and a400amps lt circuit breaker
Can we connect two CT'S to one energymeter?
we often use the word HT (high tension) line.or we say HT switch gear, whats does HT basically mean. is it different from high voltage.
what is creepage distance
Readings of ER300P Trivector meter
how to set relay setting? and example calculation...