If the circuit breaker will not close or it will trip, what
will you do?
Answers were Sorted based on User's Feedback
I can follow below trouble shooting steps,
check the error code to see if there was any short ckt or
earth fault, if there was (check for cable termination if
the connections are not burnt out due to short circuit,
check earth resistance and current voltage etc. of the
terminals) eliminate the fault then it should work fine.
Check the control wiring of the breaker check the fuses,
contactor operations etc.
check the under voltage release to see if it did not trip
due to under voltage or over voltage. check shunt trip
mechanism.
check if breaker is not overheated as a breaker may not
close if magneto thermal release is tripped.
check closing coil operation and see whether breaker gets
charged automatically with help of the motor.
if none of the above problem found, Rack out the
breaker(keep it in isolated position)trip the breaker
manually a few times and try closing it again should work fine.
In case it does not happen you can try and by pass the
breaker with help of crocodile pin Jumpers ( In case of
Emergency), but one need to be extremely careful and should
ensure that the incomer supply to breaker is turned off
while doing it, as a high risk is involved. Also you should
be confident that breaker did not trip due to an abnormal
condition.
Note: Some breakers indicate nuisance fault as well
Further,
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh arumugam
Please mention the voltage rating and the type of breaker i.e whether ACB or VCB or vcu
| Is This Answer Correct ? | 0 Yes | 0 No |
What will happen if we give 220v supply on both sides to the bulb
7 Answers Exide, Sumeet Industries, Toshiba,
what is the reason for connecting hvdc monopolar line with negative conductors
what happens when a dc shunt motor fed with an alternating suppy ?
Why does the radius of armature is less than the radius of pole shoe?
why transformer is conneted to dc for polarity test.it doesnt work in dc?
limitation of conductor height on ground when we consider EMC
What difference between voltage and current
how much Amp we can put in 1200kva generator?
Why in power plant projects we see DOL starting method used for motors upto 160 kW instead of star delta method
how to calculte capacitor range for single phase induction motors??pls tel
why the inserting resistance in wound rotor induction motor decrease the starting current and increase the starting torque
What is difference between MCB,MCCB,ELCB and RCCB? Brief description and why RCCB is costly?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)