Answer / rgs
GENERALLY TRANSFORMERS& GENERATORS ARE SUPPLIED WITH KVA
RATING AS LOAD POWER FACTOR IS NOT KNOWN.
kW = kva x pf
Prsently assuming rated voltage to be 415 v
A = 60 x 1000 / 415 = 144.
Is This Answer Correct ? | 6 Yes | 0 No |