one 60KVA UPS how can full load current tell me us formulas
Answer / rgs
GENERALLY TRANSFORMERS& GENERATORS ARE SUPPLIED WITH KVA
RATING AS LOAD POWER FACTOR IS NOT KNOWN.
kW = kva x pf
Prsently assuming rated voltage to be 415 v
A = 60 x 1000 / 415 = 144.
| Is This Answer Correct ? | 6 Yes | 0 No |
Why Current Transformers cannot be connected in parallel
Why a motor blower cobination draw more current at winter than summer?
Why AC & DC capacitor are use in UPS ??????????????????
how open delta PT works & what is its construction?
How do u analyse protection fault when vcb tripping on load
what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?
how to calculate the current carrying capacity of a 25 & 16 kva distribution transformer.
Construction of Diesel generator set?
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
415v 14kw so can u tell me how i can measure the cable size.then size of the earth also
What happens if the secondary of the transformer is shorted?
how one can check the Current of a DC 12 V battery ? Procedure. I told that take a thick wire (having more wires in it) and then join the + and - terminals of battery with the help of two ends of a thick wire .... is this correct or wrong .....
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)