what is the pre commissioning test to be carried out on LT power panel at site?
Answer / arasusulo
checking the all of bus
bars tightness and visual
short at phase to phase and
neautral...
then megger the separate
phase and ntral bus too.
then circiut braker
condition tooo.then charge
the supply and check ph
voltage and line voltage.
switch on the braker then
dstrbt the suppply by the
feeder what it is..?
| Is This Answer Correct ? | 19 Yes | 1 No |
WHEN THESE TRANSFORMERS WINDINS CONFIGURATION ARE USED? SPECIALLY EXPLAIN REGARDING STEP UP AND STEP DOWN KEEPING IN MIND.AND REGARDING LOAD ALSO. a.star to delta b.delta to star c.delta to delta d.star to star ALSO EXPLAIN WHY V USE 415/415 TRANSFORMERS IN TUBEWELLS?
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
working of diesel generator ?
what is the principle of generator , induction motor,d.c motor
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
transmisancy eficencey calculation formula
Why usually in all electrical equipment taking more current in Y pahse like pumps,compressor,or any other applications
What is the difference between online and offline UPS
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
what is meant by servo motor ? how its operating either AC or DC?
What are the types of piano switches?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)