why secondary terminal of current transformer should not be
open circuited?
Answers were Sorted based on User's Feedback
Answer / narmatha
if secondary terminal is open circuited then due to absence
of counter amp-turns of the secondary,the unopposed primary
m.m.f. will be set up an abnormal high flux in the core
which will produce excessive core loss with subsequent
heating and high voltage across the secondary terminals.
Is This Answer Correct ? | 30 Yes | 6 No |
Answer / pritesh
if we put ct secondary open circuited than no current will flow through it and also there will be high voltage across it which will damage it
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rahul
A CT Current transformer) is used to reduce the high current on primary for measuring it with small range instruments. So its number of turns on secondary will be high. So if we open circuit the secondary it will results in very high voltage on secondary which in turn damage the CT.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ayaz ahmad khan
if the secondary terminal is open then no current flow
through secondary due to absence of load
Is This Answer Correct ? | 0 Yes | 14 No |
What is the safety factor is to be consider while selecting the switchgear and protection for electrical system
I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions
If Neutral Grounding Resistor (GR) failed/shorted. Is it repairable.
Why Neutral Earthing pits and body earthing is interconnected
refrigeration cycle?
1 Answers MAHINDRA, Shapoorji Pallonji Group(SPCL),
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
Why starters are using the machines???
Pl.brief me any electrical major fault you have rectified.
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
In ac which gas will be use?
What are the effects of armature reaction on a DC machine and discuss the various methods to reduce the effect.
If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board