draw a circuit diagram connecting transformer OLTC- RTCC-
VCB-Marshalling Box otherwise Explain in words
Answer / alleysyed
OLTC stands for On Load Tap Changer, which means that a user
can change the taps of transformer winding without
disconnecting the transfomrer from the supply. Taps are
changed in order to regulate the voltage. OLTC has number of
taps . They may be 10, 11, 16 , 20 or the customer specified
rating.
Marshalling box is a box in which manufacturer of
transformer bring alarm and trip contacts signalling from
the accessories associated with the transformer. For
example, Oil temperature indicator installed on the T/F
provide a signal of alarm when the temperature of oil
exceeds the specified limit of Indicator. If temperature
exceeds more, it send the trip signal to Marshalling box,
which disconnects the transformer from main supply and
vacuum Circuit Breaker is tripped. VCB is installed on the
High Voltage side of the TF in the HV Protection panel.
Is This Answer Correct ? | 31 Yes | 5 No |
What will be the full load current of 60KVA UPS. Suggest for this formula.
How to Calculate Stc Rating of an indoor type VCB Panel? What is a full form of STC?
What is the difference between Analogue Addressable Systems and intelligent Addressable Systems
what is meant by LT & HT?
What should be the minimum depth of ground laid 66 kv ht cable?
What is the difference between diesel generator engine with and without turbo charger with the same capacity?
the winding of Gen and Motor is star or in delta ??? and why
why use only sf6 circuit breker in 400 kv sub station
I have a one P.F meter in my factory showing 2 phase leading and one phase lagging then what is my actual P.F.
What happens when DC supply is given to transformer
documented proof that aluminium bus bars are better than aluminium cables
What is the difference between Neutral and Earth