electricity board have asked me what size meter i need fitted
in my garage, its a 415volt supply and i want to run six 20amp
supplies tolifts and things plus ten florry lights , what kva
meter do i need??
Answers were Sorted based on User's Feedback
The total current will be 120A and you have to employ CT's
whose secondary current will decide the rating of meter. The
ETVM measures kva also .
Is This Answer Correct ? | 1 Yes | 1 No |
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
What do you mean by a voltage transformer?
What is the different types of cable & current capacity of cable
One 200 V, 100 W bulb is connected in series with primary of a 200 V, 10 kVA transformer. If its secondary is kept open circuited, then the bulb would have (1) Full brightness (2) Poor brightness (3) A little less than full brightness (4) More than full brightness...explain
What are the advantages and disadvantages of negative feed back?
are you hear the meaning of burden , excat meaning of burden in only one word
What is the method for testing the differential protection stabilty in generator? When the time of starting What will happen if differentail protection connection wrong means?
How to determine the Power factor is Leading,Lagging & Unity ?.I don'thave any Meters.
what is the pre commissioning test to be carried out on LT power panel at site?
Hod do u calculate cable size for underground laying and the factors effecting/influencing it??
why booster transformer is used in sumpners test conducted on transformer????
Write a note on RC operational amplifier as integrator