Answer / vachaspati sharma

your total load is :-
3TR Approx. 3000 watts
60wattx06Nos 360 watts
200Wattx02 Nos 400 watt
Cofee maker Approx 500 watt

total load 4260 watt
say aprrox 5000 watt / 1000watt
5 Kw load
KW= KVA x P.F ( if PF .8)
KVA = KW/.8
5/.8
KVA = 6 ans

Is This Answer Correct ?    3 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate the phase to phase clearness of HT /// LT bus bar?????

0 Answers  


How to calculate the load loss and no load losses of the power Transformer? i am having the following details : full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620 V for wind mill applications

2 Answers   ReasonSoft,


hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer

3 Answers   Hindalco, Piramal Healthcare,


How to caluculate number of batteries to connect a three phase ups by KVA?

1 Answers  


In radial network the source is fed from 1 end both ends at central

0 Answers  






Usage of flywheel diode in relays

0 Answers   Jindal, Voith,


which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing

0 Answers  


how can i apilly for electrical c licencese.sir,i completed B.Tech in electrical & electronics engineering in 201onot working any company

0 Answers   Subros,


which metal use as a electrical shunt?

2 Answers  


what does the word synchronous mean in 'synchronous machine'

3 Answers  


In directional earth fault protection for generator, one core balance CT is for residual current, what other CT is for, which is placed on neutral?

2 Answers  


xfhnchncv?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)