Why breakers not synchronized when the synchroscope is going
in the anticlockwise direction?
Answers were Sorted based on User's Feedback
Answer / yogesh
If the synchronoscope reads in anticlockwise direction
means the generator is running too slow. To close the
Breaker the incoming Generator frequency should be higher
than the existing Generator. Than only the incoming
Generator will take the load as soon as the Breaker gets
synchronised
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / k.prakashchandra
The power required to run at synch speed will be drawn from
the system.
Is This Answer Correct ? | 0 Yes | 0 No |
Send me Model Question paper for the post Scientific Assistant in NPCIL
what is pmg and its use
what is mean by live tank and dead tank in current transformers?
When should I use earth leakage circuit breaker for incomer and when should I use it for each feeder seperately?
Why is remote backup preferred to local backup?
what is S.D.F stands for ? (S.D.F unit 80 amp , TPN )
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
how to find the torque of the single phase synchronous motor by doing an experiment
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
how much power consumed by 1.5 ton capacity split A.C in 1 hour
CTs Ratio
what the different types of cables used for 11kv and 33kv over head work and what is the size of cable in sqmm.
2 Answers Ordnance Factories Board,