Why transformer rating in KVA?
and Generator also?
Answers were Sorted based on User's Feedback
Answer / chvnraja
Any device is rated depending on losses of the machine. In a
transformer the losses are iron losses which depends on
voltage and copper losses which depends on current so there
are no losses which depend on power factor hence transformer
is rated in KVA
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / rahul
In a transformer Losses(I^2R-Iron and Copper Losses)depends
on voltage(Volts) and current(Amps).so the rating wshould
be in KVA
| Is This Answer Correct ? | 29 Yes | 5 No |
Answer / a.muthukumar, vacon
Cu loss of a transformer depends on current and iron loss on voltage. Hence, total transformer loss depends on volt-ampere (VA) and not on phase angle between voltage and current. It is independent of load power factor. That is why rating of transformer is in KVA and not in KW.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nilamanineel@yahoo.com
but nobody did not say about alternator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepak
this is because the KVA rating give active plus reactive
power components and the reactive power is associated with
losses of the machines. KW rating tells about the power
being transfered not the losses associated with the process.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / aniket
as the is not known we cannot know the power factor so cant xpress in watts so in kva
| Is This Answer Correct ? | 5 Yes | 14 No |
How do you compute voltage drop and cable size over distance?
which type of material is used for making motor encloser
Can VFD step up to 60 Hz if it is designed to receive 50 Hz input?
difference between ceiling fan
24 Answers Altius Technologies, Raisoni, TCS, Uni Deritend,
what the main difference of the 3 phase and 2 phase power supply??
how to calc. current for 5MVAR,50hz,33kv
what is the need of capacitor in transmission lines?and how it works.
How many safety of Disel Generator
What is the differance between vacuum breaker and vacuume contactor
how to calculate of which rating transformer should be selected? take any example
WHAT IS MODULATION AND NEED FOR MODULATION ?
what is the solution for meger test failed the MV cable?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)