What is the suitable rating of MCB for 1.5 Ton A.C and why?
1Ton= how many amperes?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sahoo
20 amps is the suitable rating of MCB for 1.5 Ton A.C &
because in starting time it takes 1.5 times more current of
the full load current .1 Ton=09 amps.
| Is This Answer Correct ? | 122 Yes | 32 No |
Answer / smruti
20amp mcb is the perfect rating mcb for 1.5 ton ac due to 1.5 times of stating current.
| Is This Answer Correct ? | 44 Yes | 13 No |
Answer / vishvajeet
Because of compressor at the start current may be more than
5In , but once atrted it will take In only , os 'C' type
mcb only should be refer , now current depends upon the
watt rating so uo to 2.5kw 16 amp MCB can be used but if it
is more than 2.5 kw to 3.5 kw go with 20amp mcb only
| Is This Answer Correct ? | 34 Yes | 13 No |
Answer / ananthanarayanan
For 1.5 ton 1743 w power consumption AC, went with 16 A type C MCB.
Digital domestic House Electric meter showed around 8 Amp current for AC only.
1.5 times 8 is around 12
Hence 16 A is best for power consumption around 1743 W.
| Is This Answer Correct ? | 20 Yes | 7 No |
Answer / gautam lasgotra
For 1.5 ton ac you should use at least a 32 ampere dp mcb.
| Is This Answer Correct ? | 3 Yes | 26 No |
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?
Why current shoots up in the secondary on the knee point voltage during saturation test of CT? How core saturation effects the secondary current (while the primary side is open)? What the logic behind this?
How we calculate the current carrying capacity of H.T. cabel?
how to check ac servo motor
what is integrated ac contact circuit
How is The split core current transformer working ?
State the difference between Surge Arrester and Lightning arrester,Both are same or not?
Why winding temperature ct placed in B-Phase of the transformers??
where reactive power is used
Is it possible to operate a synchronous 2-poles turbogenerator with a still-in-place faulted bar but electrically disconnected ???? If yes, should I act on the other phases as well ???
Technical equations
what happend if we remove dc exciter from moving machine..: gg
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)