What is the suitable rating of MCB for 1.5 Ton A.C and why?
1Ton= how many amperes?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sahoo
20 amps is the suitable rating of MCB for 1.5 Ton A.C &
because in starting time it takes 1.5 times more current of
the full load current .1 Ton=09 amps.
Is This Answer Correct ? | 122 Yes | 32 No |
Answer / smruti
20amp mcb is the perfect rating mcb for 1.5 ton ac due to 1.5 times of stating current.
Is This Answer Correct ? | 44 Yes | 13 No |
Answer / vishvajeet
Because of compressor at the start current may be more than
5In , but once atrted it will take In only , os 'C' type
mcb only should be refer , now current depends upon the
watt rating so uo to 2.5kw 16 amp MCB can be used but if it
is more than 2.5 kw to 3.5 kw go with 20amp mcb only
Is This Answer Correct ? | 34 Yes | 13 No |
Answer / ananthanarayanan
For 1.5 ton 1743 w power consumption AC, went with 16 A type C MCB.
Digital domestic House Electric meter showed around 8 Amp current for AC only.
1.5 times 8 is around 12
Hence 16 A is best for power consumption around 1743 W.
Is This Answer Correct ? | 20 Yes | 7 No |
Answer / gautam lasgotra
For 1.5 ton ac you should use at least a 32 ampere dp mcb.
Is This Answer Correct ? | 2 Yes | 26 No |
A 230V, 60W bulb when connected to 230v supply what current and power will consume, if same bulb is connected to 200v what purrent and power will consume?
How we calculate the size of ht cable for any transformer
what will happen if dc supply is given to ac motor?
when a cunductor is being disconnected from live cct, still it showing charged, if its checked by line tester?
IN CABLE TRENCH WHY FILL UP THE SAND. AND WHAT IS THE DIFFERENCE BETWEEN OVER HEAD AND UNDER GROUND LAYING THE CABLES
What is the unit of inertia constant of rotating machines? Which has more inertia constant between turboalternator and hydroaltermanor and why?
could i arrange a faulty and healthey battery bank togather in parallel , if your ans is not then why?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
How would you supply a single house hold load from a 3-phase supply coming out of a sub-station?
which will glow brighter?bulb 1 (110v,100w) and bulb 2 (230v.200w) series connection
What is rotary phase converter?
Which rccb 30ma,100ma,300ma sensitivity should be used in domestic line and what is difference, advantage and disadvantage of all three