How to Calculate 11 KV Side Cable size of a 250 KVA Oil cooled transformer..

Answer / a.narasimha rao

Transformer capacity is 250 KVA

Primary current = 250000/1.732x11000= 13.12 Amps

Short circuit current ( 6 times primary current )

total current would comes -----90 amps

Size of the cable --- 3c X 35/ 50 sq.mm 11 kv HT XLPE
cable is required for primary

Secondary side current -----333.35 amps

cable size is 3.5 c X 300 sq.mm AYFY cable is required

Is This Answer Correct ?    23 Yes 15 No

How to Calculate 11 KV Side Cable size of a 250 KVA Oil cooled transformer..

Answer / pillay

IS it a 250 KVA or 2500 KVA transformer? any way you must
know the operating current first before determining the
cable size. if 250 kva than 250000 / 11000 / 1,732 = 13.12
amps the cable should be able to withstand 11000 volts and
carry 13.12 amps.

Is This Answer Correct ?    14 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

Suppose an electric motor with a controller is not working. What is the sequence of testing you will do in your troubleshooting?

2 Answers   Emerson,


what is difference between ac1 and ac3 contactor and why it is needed to be selected?

1 Answers  


L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW MOTOR STARTS WITH EARTH FAULT RELEASE

1 Answers   Ambuja,


what is power transformer?

1 Answers  


which supply is used in traction system

3 Answers  






what is the capacity of storing mass electricity.

1 Answers  


suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?

2 Answers   NHPC,


why resistive load has unity power factor,inductive load lagging and capacitive load leading power factor?

3 Answers   OEG,


i have some screw comprressor with 630kw power,i have established them with simple star to delta circuit,by the way there is so much inertia when the screw comprressors start, can you offer me contactors power with 400vac or any cataluge to choose the contactors

0 Answers  


while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva

1 Answers  


How the electric train gets the supply of electricity? What is the return path of the current?

8 Answers   Siemens,


What is stacking factor? What is its approximate value?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)