If load current is 70amps or 50amps what range of CT to
install for ampere metering
Answers were Sorted based on User's Feedback
Answer / maprayil
Always go for the CT primary suitable for about 40% higher
currents of the load current. So if the load current is
70A, you should opt for a CT primary of 98A, say 100A.
Secondary current rating of the CT will be dependent on the
input requirements of the measuring instrument (meter)/
Controller. Many such meters specially calls for an input
of 5A or 1A. Certain meters have the option to select 5A
or 1A input based on the secondary current of the CT.
Is This Answer Correct ? | 10 Yes | 1 No |
CT range is 70/5A because it caluculates min to max current
Is This Answer Correct ? | 1 Yes | 2 No |
A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of Transformer is solidily earthed) and consisting of mainly very costly and sensitive electronic equipments is giving trouble due to high voltage difference between neutral and body earth. Whether this problem can addressed by connecting neutral at the load point solidly to earth?
one cable insulation resistance 200 mega ohm. how find 250 meter cable resistance.
does the transmission line model also requier active power in no-load operation?
I decided to provide a 11KV / 440V Xformer in my Substaion. What are the protection required for that?
What do you mean by screen of power cables?
explain harmonics in simple words..........
can we use engine degreaser for electrical motors?
What is difference between VCB and SF6 breaker
what is a starter ??
why the capacity of power plant is given in MW though the generators are rated in MVA?
What is the difference between Derived earth Fault and measured earth fault.How it works.
A 10 kva ,400v/200V , single phase transformer with 10% leakage impedance draws a steady short -circuit line current of