my question is that....few days ago i had installed a three
phase motor starter for an electric saw.the motor will run
and make the hydraulic pressure which will be goes to
pressure cylender by up and down lever.two number of
limitswitches are also installed on cylinder for safety of
motor.now when the arm of cylinder reaches to the upper or
lower limit it will cut the motor's line.and motor will be
stop.now wana know that what will i do that motor runs
continue after the limitswitch cut it down but it shold not
be made any pressure.pls answer me in brief.
Answers were Sorted based on User's Feedback
The motor is driving a hydraulic pump.Install a relief valve
set at the correct pressure in your hyd system where the pump
can perform its task but when the piston reaches the top the
pressure build up will be too high and the excess pressure is
released through the valve, the limit switches wont be
necessary any more.the pump will be running all the time.
| Is This Answer Correct ? | 0 Yes | 0 No |
c0ntr0l its up and d0wn s0len0id valve thr0ugh limit switc..
| Is This Answer Correct ? | 0 Yes | 0 No |
There should be some way to vent the excess pressure built by the motor. So first of all you should have a pressure gauge or sensor to read the pressure. Then you should have either a re-circulation line in the system or vent valve to channel the excessive pressure. When the hydraulic pressure reaches a set limit the re-circulation valve should open and channel the excessive pressure back to the tank/reservoir. In this way you can keep the motor constantly on without causing damage to system.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is SF6 Circuit Breaker?
IS there any mechanical connection between the field winding and armature winding of a dc generator?
Instead of single phase(220), if we apply Phase to phase (R&Y)supply (eg: for lighting fixture). what will be the power formula?
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
what is the capital of india
13 Answers eInfochips, Reliance,
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
what will happen if OLR CT in all phases are short circuted
If the capacity of water Tank is 50000 Liters situated at 20 meters height from ground level,What would be the size of pipe and how much USGPH water will be supplied and what will be the motor or pump rating used for this work?Illustrate by showing formula?
what factors to needed while selecting a MCB and MCCB
Is current shock due to voltage or current? pls answer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)