When ct connected,that act as a stepup transformer so there will be produce a arc between the terminals of the secondary of CT.

Is This Answer Correct ?    7 Yes 4 No

Why CT's shall not be kept open?..

Answer / abdul moin

when a CT in connected to the transformer is for the
current reading to know the amps folowing through the
conductor. we keep the terminal close because of the
secondary side voltage will be rise. thats why when we
remove the meter for the maintenance purpose we provided a
short link for close the terminals inorder to avoid high
voltage at secondary.


i Hope this answer is satisfy you......

Is This Answer Correct ?    4 Yes 2 No

Why CT's shall not be kept open?..

Answer / richard harris

There is an inaccurate theory that has been in the electrical discipline for decades, and that is - if you open circuit a Current Transformer (CT) under load it can produce millions or infinite voltage.

It is the character of a CT to develop the voltage that will drive its current through its load.
(Current transformer circuits are generally a low impedance load.)

When one opens a CT circuit, to the CT - it sees an infinite resistance, and tries to develop an infinite voltage across an infinite resistance, therefore, the voltage across an open circuit CT circuit increases until the core of the CT is saturated. Once the core of the CT is saturated - it can not produce a higher voltage, - this is true for air core or iron core CTs.

There is a limit to the voltage that can be developed across a CT.

In the case of an air core CT the voltage increases until the air of the CT is saturated.
In the case of an Iron core CT, the voltage increases until magnetic flux saturates the iron.

The limiting factor in an iron core of a CT.

When the iron core of a CT becomes flux saturated, the CT like all other transformers, can NOT produce a higher voltage. The voltage that is produced is a function of how much iron is in the core of the transformer. That is true for CTs and Power Transformers.

In some cases, a higher voltage is needed to push the current through a high impedance load. To have a CT produce a higher, the CT core will need more iron in its core.

Current Transformers are rated in classes - and the higher class - the more iron in the class of the CT, and the higher voltage it can produce. That is why CTs have to be tested to determine their Saturation Voltage against their impedance load.

Plus they have to be sized not to go into saturation during a short circuit or system fault event.

Since 1978 - I have been teaching at a college, university, and professional level. I was a NETA technician level 3 for many years, and every thing that I have taught I have had field hands on experience.

The reason that I am responding to this question, as I have never had anyone accurately explain about why not to open a CT circuit "underload." - yes you can open a CT or CT circuit ONLY if it has no load or current going through its circuit.

In teaching an Electrical Safety class on a telephone conference with 25 individuals - some when back and told the Operations Supervisor and he came and confronted me. Even Electrical Engineers and management technical have never explained it or understood it to the point that they could explain it to me.

I hope this short explanation answers your question as to why a Current Transformer, or its circuit should not be opened under load.

Should you have any additional questions, do feel free to ask.

Richard Harris

Is This Answer Correct ?    1 Yes 0 No

Why CT's shall not be kept open?..

Answer / abhishek goyal

CT always connecting into the series position. If we have
some work on the Meter, we need to short the CT terminal. If
CT in open condition (it can't connected to the meter)its
step down the current in terms of 300/5AMP (for example).
After few second or minute it will drawn the more current at
infinite level at that time CT temperature also increase. If
we can't short the CT it will make big blast or sever
damage.

Is This Answer Correct ?    0 Yes 0 No

Why CT's shall not be kept open?..

Answer / azhar ali

Basically, current transform has a few turns one or may be two at primary sides and many turns on Secondary side.If the ammeter is removed, the secondary winding becomes open-circuited and the transformer acts as a step-up transformer due to the very large increase in magnetizing flux in the secondary core. This results in a high voltage being induced in the secondary winding equal to the ratio of: Vp(Ns/Np) being developed across the secondary winding.
Turn ratio=vp (NS/Np)=> VP=480 NS=160 V &Ns=1 Then,
Tr=480*160/1 = 76800 volts
So it will be very dangerous if the secondary is opened.Therefore short the secondary of CT if the current meter is removed from the CT having primary current.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate meter constant @ HT yard

5 Answers   Juniper Networks,


how electrical earthing maintenance done in industry?

0 Answers   L&T,


How can Inductive load reduce the line voltage of HV transmission line and vice versa Capacitive load?

1 Answers  


How to Measure A.C Resistance for Earthing ?

2 Answers  


What is DG B-check and C-Check

1 Answers  






What is the difference between EXE and EXD

1 Answers  


difference between converter and invertor

2 Answers  


how to calculate micom relay earth falt time and current sertting

0 Answers  


send me all basic electrical question and answers

0 Answers  


Car battery + terminal allways biger than - terminal! Why?

2 Answers  


how to calculate the change over time for star delta starter for different KW motor?

0 Answers  


what is difference between inductive and reactiveload?

5 Answers   ONGC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)