why single phase induction motors are not self staring ?
how can we start the 1-phase Induction motor ?
Answers were Sorted based on User's Feedback
Answer / ajith
the 1ph supply applied to stator wdng cant produce a
rotating magnetic field as in the case of a 3ph induction
motor..
if a 1ph is applied to the induction motor the resulting
magnetic field is only altrnating (not rotating)..
In order to make the 1ph induction motor self starting...,
2 windings are used ..startin windin n runnin wdng..called
split phase motor.. or by connectin a capacitor in series
with the start wdng.. for obtainin necessary phase
diplacement...
Is This Answer Correct ? | 38 Yes | 2 No |
Answer / abhimanyu kumar gupta
Single phase IM given single phase supply given to stator
winding an alternating magnetic field develop in stator and
produce alternating flux and collides with rotor winding and
produce induced EMF at rotor since the rotor winding are
closed this produce induced current in rotor.
Due to this induced current in magnetic field of alternating
nature and this nature is not rotating. Both magnetic field
in stator and rotor are Colline's so resultant torque rotor
will 0. Hence single phase IM does not self start.
In order to make motor self start an external force to the
rotor should be given because of locking of field will
disappear.
Is This Answer Correct ? | 3 Yes | 2 No |
Whats the principle of lightning? How protection against lightning is achieved? Types of protection? How to select the height of lightning spike? as per the area.
whats the existence of reactive power and when it arises?
pls give proper discription of selection of transformer based on particular load.
in dc suppy frequency is zero why? if dc frequency is zero how to exist dc transients and ac transients
What is meant by stator? What is meant by rotor?
How to calculate the KA rating for a circuit breaker if we know the KVA rating of the generator feeding it?
why can't we increase the voltage by increasing the field voltage in order to get higher voltage.so that we can eliminate step up transformer
what is purpose of manual bybass in ups
in 33kv/11kv stepdown t/f why should we use Star point
what could be the reason of a burnt current transformer in an electrical panel
What is the difference between Earthing and Neutral?
What is encoder, how it function