hi frienda We have 250kva cater pillet dg set we are fasing
one diffrent proublam in dg we are start dg set after one
mint applying load around 450a load but dg was run 3 Or 4
mints after 3 mints dg was shuding down automatic how to
face this proublam pls tel any budy
Answers were Sorted based on User's Feedback
Answer / abdulgafar
A full load current of 250KVA DG Set is approximatly 350A.
Most of the DG Sets are designed to catter approximatly 10%
over load For a period of one hour hence a 250KVA dg set
can catter 385A For a period of one hour. you have applied
more load then the DG Set can catter/ deliver hence your DG
Set is triping automatically after about 3 min. hope i have
answered your question.
AGM
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ajay
that is 250kva d.g.it will be give only 250-300amps
load...you will also give to 300a load and then check it
OR
hydrollic magnatising is very low,d.g.will run there
after voltage is not buildup,then d.g.is shuting down...
please do one thing short your battery
terminals and then give to connection it will be started.
Is This Answer Correct ? | 0 Yes | 0 No |
what is differance between dirty earthing and clean earthing and their applications
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
I completed iti in2004 I was worked in A grade contractor can I get c licence
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is onbserved the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
how to calculate the voltage drop in electrical cable while laying cables?
What is triac?
I have a table fan of Rallifan Make. When I overhauled it I found a stator winding and an aluminum die cast rotor. So it is supposed that it is a 1 phase induction motor. But there are only two terminals coming out and there is no capacitor. Can any one tell how this motor works? or which type of this motor is?
Stator core loss of squirrel cage induction motor compared to rotor core loss is= A equal B more C less D depends on load
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
how the vaccum ckt breaker workes..? how the arc is quenching in it?
how to make a solar panel? why solar panel cell connected to serious?
What is transient Phenomenon?