why we are used armed coble for wiring of 3phase motor?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Armoured cables are used to protect cables from
physical/mechanical injuries
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / arun
answer 2 is partially correct but i would like to add one more point i.e armour is not only used for mechanical strength and it is also used for earthing i.e if any leakage occurs than that leakage currect will be earthed through this armour
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pillay
3 phase motor can be cabled by any method provided
it provides the necessary safety at site and meets the
requirements of the regulations.
armoured cable is more often used because it is a faster and
a cheaper method that meets the requirements to connect a motor.
Is This Answer Correct ? | 0 Yes | 5 No |
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
Can any one help me how to set an overload set the range from 2.8A to 4A , rated motor current 22A, CT 60/5A
will the turbogenerator operate on leading power factor with out modification in the stator winding.
Two electrically operated Vibro Motors are fixed in parallel direction in vibrating feeder. What is the direction of both Vibro Motors?
What are locations arc protection relay is fixed.
what should be the no load current of an induction motor
sir, Is their any measuring unit of knoking? please explian?
why do we use star-delta starter. what is its need?
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?
What is the technical name of Transformer Oil ?
17 Answers Bhel, Don Bosco, Lanco,
How we can calculate the Amps for the cable Ex:- For 1sqmm wire how many amps we can draw (calculation)
I have installed capacitor bank at secondary transformer. cos phi is increase. but on load (far from transormer), it still poor. Can anybody explain it??